Skip to main content

Utility network trace types

The utility network offers a variety of core trace types. Certain trace types use the tier definition of a traditional domain network and incorporate the subnetwork definition, while others do not take subnetwork properties into account. Each trace type can be adjusted to refine the results by specifying additional configurations on the Trace or Add Trace Configuration tools. Review each trace type below to learn more.

Subnetwork-based traces are supported with traditional domain networks. These traces rely on information from the underlying Domain Network and Tier parameters specified in the Trace tool to influence the trace results.

Each tier has a subnetwork definition that controls the properties or configuration of subnetworks participating in the tier. The subnetwork definition for the Tier parameter is used to preconfigure the trace with default settings. In addition, subnetwork-based traces are influenced by terminal configurations (valid paths and directionality). To learn more, see Connectivity and traversability.

Subnetwork-based traces that use the subnetwork definition in the trace configuration are supported with traditional domain networks only. These include the following:

Network traces that do not rely on the subnetwork definition are supported with both traditional and telecom domain networks. These include the following:

Circuit traces that rely on the presence of a circuit definition are supported with telecom domain networks only.

Note:

Upstream and downstream traces do not use the subnetwork definition when the Use Digitized Direction parameter is checked and can be run with both traditional and telecom domain networks.

To promote accurate trace results, ensure the network topology has been validated, is clean, and contains no dirty areas for the areas of the network that will be traced. Trace results are not guaranteed to be accurate if dirty areas are present. Other than a visual inspection of the map, you can determine whether dirty areas are present in your network by using the Validate Consistency configuration option on the Trace tool or by checking the Dirty Area Count property on the network properties tab of the Layer Properties dialog box.

Learn more about tracing utility networks and how to configure a trace.

The subnetwork-based traces identified above rely on subnetwork information. If a subnetwork is dirty or invalid, the trace could fail due to the presence of dirty areas or subnetwork errors. To determine whether a subnetwork is dirty or invalid, inspect the Status (ISDIRTY) attribute in the Subnetworks table. Depending on the version of the utility network dataset in use, the domain values may be presented as either Dirty or True for dirty, Clean or False for clean, and Invalid for invalid subnetworks. To clean a dirty subnetwork, use the Update Subnetwork tool. Invalid subnetworks indicate that additional steps are required to modify features and update the subnetwork status so it can be cleaned. To learn more, see Subnetwork status.

Note:

When working with an enterprise deployment, the Trace tool can only be used with a utility network feature service.

Find connected features

A connected trace begins at one or more starting points and spans outward along connected features. A trace traveling along a path stops when either a barrier is encountered or there are no more connected features (end of a path). This type of trace is useful for checking that newly edited features have expected connectivity after editing.

Example of a connected trace

This type of trace travels the network based only on connectivity. It does not make use of the subnetwork definition in traditional domain networks, nor does it support terminal directionality or valid paths. The trace configuration must be manually configured to control the traversability of this type of trace on the Trace tool. For example, instead of returning all connected features, you could return all connected features of a particular output asset type (pad-mounted transformers) that meet a specified output condition (greater than 35 kVA) and use a function barrier to stop the trace when the sum of the transformer loads reaches 1,000.

See Find connected features for more details.

Note:

Subnetwork controllers are not required for a connected trace.

Trace a subnetwork

A subnetwork trace discovers all features participating in a subnetwork. Subnetwork traces require one or more starting points or a subnetwork name to determine which subnetwork to trace.

Example of a subnetwork trace

The trace begins at one or more starting points and spans outward along connected features to find subnetwork controllers that are traversable. Once a subnetwork controller is encountered, the trace spans outward from that controller along the subnetwork. A subnetwork trace stops when either a barrier or a network feature that is not traversable is encountered, or when there are no more connected features. This trace type is useful for validating whether subnetworks, such as circuits or zones, are defined appropriately.

Dive in:

When the Subnetwork Name parameter is specified, the subnetwork controller or controllers for that subnetwork are used as starting points for the trace, and the Starting Points parameter is ignored. The feature representing the subnetwork in the SubnetLine feature class is also returned in the trace results if no output filters are specified.

Although this type of trace uses the tier's subnetwork definition to automatically populate parameters, further configuration can be done using the Trace tool. For example, instead of tracing an entire subnetwork, you can configure the trace to stop at valve features with a certain pressure value using a condition barrier.

Subnetwork traces in hierarchical domain networks will traverse through controllers that have different tiers and only stop at controllers with the same tier as the input tier. To stop traversal of a subnetwork trace based on tier groups, additional configuration is needed. A network category or network attribute can be created and assigned to boundary subnetwork controller devices for different tier groups, and these can be configured for the trace in the Traversability section of the Trace tool. Terminals can impact a subnetwork trace by restricting flow when traversing certain terminal paths through a device based on directionality of the trace. To learn more, see Connectivity and traversability.

Subnetwork traces require a subnetwork to be free of dirty areas; therefore, it is recommended that you update subnetworks before running a trace operation.

Tip:

You can also perform a subnetwork trace using the Trace Subnetwork Trace Subnetwork context menu option on the Find Subnetworks pane.

See Trace a subnetwork for more details.

Locate subnetwork controllers

A subnetwork controller trace is helpful to locate all subnetwork controllers for the traceable subnetwork. The trace begins at the starting point and spans outward to find the subnetwork controllers to return as the trace result. These are returned as a selection set by default.

Since this is a subnetwork-based trace, it uses the tier's subnetwork definition in a traditional domain network and is influenced by terminal configurations. To learn more, see Connectivity and traversability.

Subnetwork controller example

Subnetwork controllers associated with a subnetwork are those that have a path to the starting point and have the name of the subnetwork stored in the Subnetwork name attribute. This can include boundary features such as tie switches in electrical networks that bridge the boundary between two subnetworks.

Locating subnetwork controllers requires a subnetwork to be free of dirty areas. It is recommended that you update subnetworks before running a trace operation.

Tip:

You can also select subnetwork controllers associated with a subnetwork using the Select Subnetwork Controllers Select Controllers context menu option on the Find Subnetworks pane. This operation does not perform a subnetwork controllers trace but instead selects the valid (active, non-deleted) controllers associated with a selected network from the Subnetworks table.

Learn more about how to locate subnetwork controllers

Find upstream or downstream features

By default, the upstream or downstream direction of a subnetwork is determined on the fly during a trace. This is done by discovering whether the domain network is source- or sink-based and by locating the subnetwork controllers. When modeling flow using subnetwork controllers, upstream traces travel toward subnetwork controllers in source-based domain networks and away from subnetwork controllers in sink-based domain networks. Likewise, downstream traces travel away from subnetwork controllers in source-based domain networks and toward subnetwork controllers in sink-based domain networks. Terminal configurations influence these trace types.

You can perform a subnetwork, upstream, or downstream trace using the Connectivity, Elements, or Features result type options with the Include flow directions parameter to return flow directions derived from subnetwork controllers in the result to a .json file

Alternatively, if you use a model that relies on the digitized direction of lines to determine the direction that resources flow in the network, the Use Digitized Direction parameter can be used with upstream and downstream traces. This approach determines flow using the digitized direction of the line or the From and To global ID of the edge object in the association, and the Flow direction attribute. When the topology is enabled or validated, line features and edge objects in the domain and structure networks have flow direction established with the digitized direction of line features, and with direction of the From and To global ID of the edge objects in the association by default.

Learn more about flow direction in a utility network

Note:

When loops are encountered during an upstream or downstream trace, trace results will return all features in a loop unless devices with a directional terminal configuration are present or Allow Indeterminate Flow is unchecked.

Both of these trace types travel the network based on traversability and require the subnetwork to be free of dirty areas. It is recommended that you update subnetworks before running a trace operation if they are dirty.

Downstream trace

When modeling flow using subnetwork controllers, the subnetwork controller must be identified from the starting points to establish flow direction and perform a downstream trace. Once identified, downstream traces travel away from the subnetwork controller, with flow direction, from the starting points in source-based networks and toward the subnetwork controller in sink-based networks.

When modeling flow based on the digitized direction of lines with the Use Digitized Direction parameter checked, subnetwork controllers are not taken into account and flow direction is based on the digitized direction of the line and the Flow direction attribute.

In both cases, if a barrier is encountered or there are no more connected or traversable features, the trace stops. Network features between the starting points and downstream end locations are returned. In a traditional domain network, if the starting point originates within a mesh, the entire mesh is included, as well as network features downstream from the network protectors that delineate the mesh.

Example of a downstream trace in a source-based network

Upstream trace

When modeling flow using subnetwork controllers, the subnetwork controller must be identified from the starting points to establish flow direction and perform an upstream trace. Once identified, the upstream trace travels toward the subnetwork controller from the starting points, against flow direction, in source-based networks and away from the subnetwork controller in sink-based networks.

In a traditional domain network, if the starting point originates within a mesh, the entire mesh is included, as well as network features upstream from the network protectors that delineate the mesh. When a barrier or the end of a path (either no more features, or where another subnetwork begins) is reached, the trace stops. Network features between the starting point and the barriers or end of a path are returned in the results.

Example of an upstream trace in a source-based network

When modeling flow based on the digitized direction of lines with the Use Digitized Direction parameter checked, subnetwork controllers are not taken into account and flow direction is based on the digitized direction of the line and the Flow direction attribute. This is supported with both traditional and telecom domain networks.

Note:

The Use Digitized Direction parameter is available with Utility Network Version 7 and later. When working in an enterprise deployment, this requires ArcGIS Enterprise 11.3 or later.

Configurations on the Trace tool can be used to modify an upstream or downstream trace. If you configure the trace to span multiple tiers, network features from subnetworks in other tiers are returned (provided they are upstream or downstream). This is done by defining the Target Tier parameter for a trace.

An example of a modified upstream trace includes returning only upstream protective devices. A modified downstream trace example is a downstream trace spanning three levels run on an electrical domain network with three tiers: distribution (Tier), subtransmission, and transmission (Target Tier).

See Find upstream and downstream features for more details.

Detect loops in your network

Loops are areas of the network where flow direction is ambiguous. Within a loop, resources can flow in either direction. Loops are expected with mesh networks but usually indicate error conditions in radial networks. You can discover loops using the Trace geoprocessing tool with the Loops trace type set.

Example of loops trace

This trace begins at a single starting point and spans outward based on connectivity. Features participating in loops are returned as a single selection set. To augment the trace to travel the network based on traversability, parameters on the Trace tool can be set, making it an advanced loops trace. For example, configure the trace to detect loops in a set of electrical conductors for a certain phase.

See Discover network loops for more details.

Discover the shortest path

Identify the shortest path between two starting points using a shortest path trace. The shortest path is calculated using a numeric network attribute such as shape length. Cost- or distance-based paths can both be achieved using this type of trace.

Important:

The shortest path trace type is deprecated with ArcGIS Pro 3.7 and ArcGIS Enterprise 12.1. While the shortest path trace will continue to function and be an option until the next major release, it is recommended to use the path trace to return the shortest path. The path trace provides the same functionality to return a shortest path result while offering additional capabilities to find paths in your network.

Note that the path trace is not currently supported across all platforms. Some clients, APIs, and SDKs will adopt support for the path trace in future releases.

Example of shortest path trace

A shortest path trace does not use a subnetwork definition and does not require subnetwork controllers. This type of trace is supported in both traditional and telecom domain networks and runs based on connectivity, with the exception of terminal paths. To incorporate traversability into this type of trace, parameters on the Trace tool can be explicitly set, making it an advanced shortest path trace. Advanced shortest path traces allow you to do such things as find the shortest path through 18-inch pipes between two points in a gas network.

The shortest path trace is subject to terminal paths, but not terminal directionality. When a terminal device is traced, the valid paths set for the device are respected. For example, a shortest path trace comes across a bypass switch in an electrical network. Valid paths for the bypass switch have been established, so the trace travels through the device along the valid paths; traces will not travel paths that are not valid. To learn more, see the Bypass switch example in Terminal management.

See Discover the shortest path for more details.

Discover valid paths

Use a path trace to find valid paths that exist between one or more start and stop locations. A path trace begins at a start location, designated using starting points to identify the origin of the path to be analyzed. Stop locations specify the end of the path and can be designated explicitly using stopping points, by a line or edge object terminated by a system junction with a valence of 1 (also known as an unterminated edge), or in a telecom domain network by features or objects with asset types assigned the Circuit Location network category.

The Num Paths and Max Hops parameters can be configured to constrain the number of valid paths returned as well as the total number of hops allowed between edges in a path. As an example, the below image displays a path trace between a defined starting and stopping point where the Num Paths and Max Hops parameter values are set to 5. With this configuration, the path trace returns two valid paths between the provided trace locations. Increasing the Max Hops parameter value to 6 would return two additional paths for a total of four valid paths.

Example of a path trace

When a path trace is configured using the Shortest Path Network Attribute Name parameter and a Num Paths parameter value of 1, the shortest path can be returned. See Return the shortest path for more details.

The path trace does not use a subnetwork definition and does not require subnetwork controllers. This type of trace runs based on connectivity alone, with the exception of terminal paths and can be used with traditional and telecom domain networks. When working with telecom domain networks, the Infer Connectivity parameter can be used to find paths and model circuits using connectivity inference when explicit physical connectivity is not present. To incorporate traversability into this type of trace, parameters on the Trace tool can be explicitly set, making it an advanced path trace.

See Discover valid paths for more details.

Locate isolating features

An isolation trace is used to determine the minimum set of operable features required to stop a network's resource, effectively isolating an area of the network. For instance, when a leak occurs on a water network, particular valves must be closed to eliminate water flow at the leak location. This prevents damage and allows field crews to safely start the repair process.

Example of isolation trace

The Isolation trace type can find point and line features that isolate an area of the network in a traditional domain network. For example, in a gas network, pipes can be pinched to stop the flow of gas at the leak location.

As a subnetwork-based trace, the Isolation trace type uses the subnetwork definition set for the input tier. The trace begins at one or more starting points and spans outward along traversable features. The trace stops when either a barrier or a feature that is not traversable is encountered or when there are no more connected features.

An isolation trace requires that a filter barrier be defined in the trace configuration to help pinpoint which features are isolating the starting point or points. This uses a specific network attribute or network category to stop the trace. For example, a filter barrier can be used with Category = Isolating. In this example, Isolating is a user-defined network category that is assigned to specific asset groups and asset types that are considered isolating. Additional filter barriers can be used to return valves with specific properties. For example, you can choose to return only accessible and operable valves: ones that are not paved over or rusted shut.

To include all of the isolated features in addition to the isolating barrier features, check the Include Isolated Features check box. For example, the valves or pipes that are isolating the leak location, plus all isolated features, will be returned. When checked, the trace results will include all features in the isolated area. The Include Barrier Features check box can be used to include or exclude the isolating barrier features in the trace result.

To refine the type of isolating features that are discovered during a trace, the Output section of the trace configuration can be used. For example, you can choose to return only bypass isolation valves.

See Locate isolating features for more details.

Return circuit information

Return a circuit in your telecom domain network using either a circuit name or one or more starting points using a circuit trace. Unlike other trace types which depend solely on connectivity and traversability in the network, the circuit trace uses the network topology as well as the circuit management tables to identify the elements which comprise a circuit. This provides the unique ability to handle discontinuities between, or within sections to return both physical and virtual circuits and sections even in cases where no physically connectivity exists due to gaps or virtual sections.

A circuit trace can be returned as a selection, as aggregated geometry, or as a circuit definition with the option to include geometry for path connectivity to a .json file. When circuit results are returned as a selection result, the Include Containers parameter can be checked to return a selection in the map for nonspatial objects contained by spatial features. Virtual circuits and virtual sections are not displayed in the result as they are not physically present in the network; however, the features associated with the start and stop location of a virtual circuit or section are returned.

The aggregated geometry result type allows you to return a multipart geometry representing the entire circuit and can be used in conjunction with the Synthesize Geometries parameter to return geometry for a nonspatial circuit using the spatial container's geometry. When you use the Circuits result type, this returns the circuit definition to an output .json file along with the option to include geometry for path connectivity information for the circuit and circuit sections when used with the Include geometry and Synthesize Geometries parameters.

The circuit trace is supported for use with telecom domain networks only. To incorporate traversability into this type of trace, parameters on the Trace tool such as feature or condition barriers can be explicitly set, making it an advanced circuit trace.