Analyze and address errors
The Migration toolset in the Utility Network toolbox contains three tools that provide a simplified process for the migration of existing data into a utility network to support basic editing and tracing workflows.
The Analyze Network Data tool evaluates an input utility network to find common types of topological inconsistencies, including self-intersecting lines, stacked points, and invalid connectivity. The tool generates a mobile geodatabase as an output that contains various feature classes and tables, which describe the error types found in the data. You can use these output feature classes and tables to understand the error scenarios and define the actions that you must take for each error type. The output Error Resolutions table can be edited and used to address error scenarios as the input for the Apply Error Resolutions tool.
Learn more about migrating to the utility network
Requirements
The following requirements must be met to analyze network data and find common error types:
  • The network topology can be enabled or disabled.
  • The following requirements must be met when working with an enterprise geodatabase:
    • When working with an enterprise geodatabase, the Input Utility Network parameter value must be from a database connection established as the database utility network owner.
Analyze network data to find errors
To analyze network data for common error types, complete the following steps:
  1. On the Analysis tab, in the Geoprocessing group, click Tools to open the Geoprocessing pane.
  2. In the Geoprocessing pane, search for and select Analyze Network Data.
  3. For the Input Utility Network parameter, specify a utility network.
    Utility networks from a feature service are not supported.
  4. For the Output Location parameter, provide the path to a folder that will contain the output mobile geodatabase.
  5. For the Output Name parameter, specify the name for the output mobile geodatabase.
    The default is AnalysisResults.
    A folder is created that contains a mobile geodatabase with the name specified for the Output Location parameter.
  6. For the Set default resolution actions parameter, specify whether the default Action attribute values will be populated in the Error Resolutions table for the specified error types.
    Any error action values populated by the tool can be modified. Not all errors have a default error action.
    • Checked—The following error types will be populated with the default resolution action in the Action field of the output Error Resolutions table:
      • Empty geometry—Delete all.
      • Empty Shape length—Delete the row from the feature class.
      • Self-intersecting line—Delete all but first vertex.
      • Duplicate vertices—Delete all but first vertex.
      • Stacked points—Delete all but first vertex.
      • Multipart—Cut.
      • Vertex within tolerance—One Anchor is assigned based on priority (junction > endpoint > midpoint) and Snap is assigned for all others.
    • Unchecked—No error types will be populated with default error actions in the output Error Resolutions table. This is the default.
    Learn more about the available error actions
  7. Click Run.
The Analyze Network Data tool completes and creates a mobile geodatabase in the output location specified. The Error Summary and Error Locations feature class and Error Resolutions table are added to the active map using a group layer.
Feature class and table outputs
The mobile geodatabase created by the Analyze Network Data tool contains the following feature classes and tables:
  • ErrorLocations—Point feature class describing distinct locations in the network where errors were discovered.
  • ErrorSummary—Multipoint feature class summarizing all unique combinations of errors in the network using a multipart feature.
  • ErrorRecords—Table containing information about all the features present at each error location and the type of associated error.
  • ErrorResolution—Table describing the resolution for each group of errors. This is used as the input for the Apply Error Resolutions tool.
The folder containing the mobile geodatabase also contains a layer file (.lyrx) and a .csv file that can be used to understand and resolve errors:
  • A group layer symbolizing errors found within the input utility network. The name of this group layer will match the name provided for the Output Name parameter when running the Analyze Network Data tool. This layer uses other tables and feature classes in the mobile geodatabase to aid the visualization of errors in the map.
  • RuleCandidates—A .csv file communicating potential utility network rules that could be added to resolve errors.
The feature classes and tables in the output can be overlaid with a utility network using the group layer to provide context and aid visualization of the various errors encountered. The sections below outline the various output classes and their schema.
Error Summary and Error Locations feature classes
The Error Locations and Error Summary point feature classes provide information about the errors discovered in the input utility network. The Error Summary feature class contains multipoint geometries that aggregate all like features in the Error Locations feature class with a shared Analysis types and Error code value to provide an overview of the different error types in the utility network by class, asset group, and asset type.
The Error Locations feature class contains a point feature for every location in error. This allows you to review the individual locations represented by the Error Summary multipoint feature. When you select a location feature, related records are also selected in the Error Records table.
Selecting a record in the Error Locations feature class adds the source feature class to the map if it's not already present and selects related features. This relationship uses an absolute path to the source data. The relationship must be updated if the source data is moved.
The Error Summary feature class contains the following attribute fields:
Field name
Field alias
OBJECTID
Object ID
The object ID for the multipoint error summary feature.
ErrorCode
Error code
The error code for the summarized error type.
AnalysisTypes
Analysis types
The feature class, asset groups, and asset types that are present at this location. This includes the feature in error and coincident features.
Tip:
In Options, adjust the Row Height setting to Triple on the Table tab to improve the readability of this field.
TypesInError
Types in error
The feature class, asset group, and asset type of the features in error.
SourceName
Source layers
The feature class of the features in error.
AssetGroupName
Asset groups
The asset group of the features in error.
AssetTypeName
Asset types
The asset type of the features in error.
Occurrences
Occurrences
The number of Error Locations features that make up the multipoint geometry for each unique combination of AnalysisTypes and ErrorCode field values.
ResolutionKey
Resolution key
The relational key used to link the Error Summary feature class to the Error Resolution table. Selecting a multipoint feature in the Error Summary feature class selects the related records in the Error Resolution table.
Shape
Shape
The location of the features.
The Error Locations feature class contains the following attribute fields:
Field name
Field alias
OBJECTID
Object ID
The object ID for the individual error in the utility network.
ErrorCode
Error code
The error code associated with the feature in error.
AnalysisTypes
Analysis types
ResolutionKey
ResolutionKey
The relational key used to link the Error Locations feature class to the Error Resolution table.
SHAPE
Shape
The location of the feature.
Error Records table
The Error Records table contains detailed information about features related to each error present in the Error Locations table. The group layer added to the map contains a subset of records from this table for every feature class containing errors filtered using a definition query. This table can be helpful when evaluating which other features may have contributed to the error condition reported.
The Error Records table contains the following attribute fields:
Field name
Field alias
OBJECTID
Object ID
The object ID for the error record.
LocationKey
Location key
The location key value for the error records. This corresponds to the object ID for the feature in the Error Locations feature class.
ErrorCode
Error Code
AnalysisTypes
Analysis types
ClassGroupType
Feature type
The feature class, asset group, and asset type of the associated feature.
SourceID
Source layer
The feature class that is associated with the error record.
SourceOID
Feature ID
The object ID of the feature associated with the error.
The Error Resolutions table is an editable table used to define the corrective actions that you must take to resolve the errors found by the Analyze Network Data tool. The modified table is then used as the input for the Apply Error Resolutions tool to edit features and correct error scenarios.
The Error Resolutions table contains the following columns:
Field name
Field alias
OBJECTID
Object ID
The object ID of the resolution record.
ErrorCode
Error code
AnalysisTypes
Analysis types
Tip:
ResolutionKey
Resolution key
The relational key that relates to the Error Summary feature class.
GroupPosition
Group position
The sequence of the row in the Analysis types group.
ClassGroupType
Feature type
The features class, asset group, and asset type of the features in error.
SourceNames
Source layer
AssetGroupNames
Asset group
The asset group of the feature associated with the error record.
AssetTypeNames
Asset type
The asset type of the feature associated with the error record.
ErrorContext
Context
Specifies whether the record references a feature in error or a coincident feature provided for context.
ErrorAction
Action
The corrective action to be performed to resolve the error type. The options are as follows:
  • Do nothing—No action is taken to resolve the error. This is the default.
  • Update all—Update all vertices or features at the location.
  • Update all but first—Update all vertices or features except the first one at the location.
  • Delete all—Delete all vertices or features at the location.
  • Delete all but first—Delete all vertices or features except the first one at the location.
  • Create—Create a new feature. When this action is chosen, you must specify the type of feature that will be created using the Create/Update type attribute field.
  • Anchor—Set the location as an anchor point to which other vertices will be snapped.
  • Snap—Move the vertices at the location to snap with an anchor point at the same error location.
  • Cut—Cuts the line at the vertex where the error occurs.
DeltaX
Delta X
The offset value applied to the x-coordinate of the geometry of a point or the vertex of a line. This is only valid for an update or create action.
DeltaY
Delta Y
The offset value applied to the y-coordinate of the geometry of a point or the vertex of a line. This is only valid for an update or create action.
DeltaZ
Delta Z
The offset value applied to the z-coordinate of the geometry of a point or the vertex of a line. This is only valid for an update or create action.
DeltaStep
Delta step
When there are multiple features present in the same location, this defines the offset value applied to the DeltaX, DeltaY, and DeltaZ fields for each subsequent feature. This is only valid for an update or create action.
ActionClassGroupType
Create/Update type
The asset group and asset type to use when creating a new feature or updating an existing feature.
Error types found using the tool
While the Analyze Network Data tool is not intended to identify all errors, the following common utility network error types are found and returned in the Error codes attribute field in the Error Summary and Error Locations feature classes and Error Resolutions table. The table below outlines the error codes that may be found by the tool, the associated error ID, a description of the error, and the action (when applicable) that can be applied to resolve the error in the Error Resolutions table.
Not all error types have an automated solution available.
Learn more about the best practices for fixing connectivity errors in a utility network
Error code
Associated error ID
Available error action
Empty geometry
The geometry for the network feature is empty. This error can occur when a line feature has a zero or near-zero length.
Delete all/Delete all but first (vertex)
Unknown asset group
The subtype used for the asset group attribute is unknown. This error occurs when a feature is migrated into the Unknown asset group.
Update all
Shape length
The line feature has length within the tolerance. This error can occur when a line feature has a zero or near-zero length.
Rule missing
8
Connectivity exists between junction and edge features without a required junction-edge rule. This error does not consider junction-junction, edge-junction-edge, structural attachment, or containment rules.
N/A
Ambiguous connectivity
9
There is more than one rule available for a potential connection. It is also possible to receive this error if more than one device exists at the endpoint of a line.
N/A
Missing junction
10
Invalid connectivity exists due to line features that are connected between different asset groups and asset types without an intermediate device or junction feature.
Create
Edge connectivity policy
13
A line has a connectivity that violates its edge-connectivity policy. For example, a line feature that only allows endpoint connectivity has a point or another line feature placed midspan.
N/A
Multipart
19
A linear network feature has multipart geometry.
Cut
20
A line feature loops back and overlaps itself at the intersection of two vertices.
Cut
Duplicate vertices
21
A linear network feature has multiple vertices existing in the same x, y, z location or within the network tolerance.
Invalid asset type
23
A network feature has an asset type other than the defined asset types for the asset group it belongs to. This error occurs when the asset type value of a feature is not a valid value in the asset type domain for the asset group.
Update all
Invalid asset group
23
A network feature has an asset group with a value outside of the range for the subtype, or the subtype is invalid. This error occurs when the asset group value of a feature is not a valid subtype for its class.
Update all
Stacked points
25
Two or more points are geometrically coincident or within the network tolerance. For example, a service point and a voltage regulator have the same x, y, z coordinates.
Invalid terminal
36
The line feature has an invalid terminal. This occurs when the from terminal ID or to terminal ID attribute for a line is not valid for one of the connected devices.
N/A
Subnetwork tap
37
A feature with the subnetwork tap category is drawn at the end point of two lines.
N/A
Midspan terminal device
38
A device with multiple terminals cannot be midspan along a line. This occurs when a terminal device is drawn midspan on a line.
N/A
N/A
Two or more vertices from separate features are within the spatial tolerance of the dataset but are not topologically coincident.
Anchor
Snap
Available error actions
The following table describes the actions available to address errors using the tool
Action
Create
Create a new feature. When this action is selected, you must specify the type of feature using the Create/Update type field.
Update all
Updates the corresponding vertex or features. If there are multiple features associated with the fix, you can choose to update all features or update all but the first feature.
This action can also be used to update the location of a feature using the DeltaX, DeltaY, DeltaZ, and DeltaStep fields. When there are multiple coincident features, specify a value for the DeltaStep attribute to ensure each feature is offset from the previous feature.
The asset group or asset type of a feature can also be changed using the Create/Update type field.
Delete all
Deletes the corresponding vertex or features. If there are multiple features associated with the fix, you can choose to delete all features or vertices or to delete all but the first feature or vertex.
Anchor
Snap
The Anchor and Snap actions are used to resolve the Vertex within tolerance error. The Anchor action defines one vertex or feature as the anchor location while Snap communicates the other vertices or features to be snapped to the anchor location.
Cut
Cuts the line at the vertex where the error occurs. When used to address self-intersecting lines this shorten the existing line feature and create a new line feature for the remaining geometry. When used to address multipart geometries, this action creates single-part features with attribute values matching the original feature.
Define error resolution actions
The Error Resolutions table is used to define the corrective actions that you must take for the various errors found by the Analyze Network Data tool.
For an example, to define the actions needed to resolve a self-intersecting line error, complete the following steps:
  1. Add the utility network and all associated classes to an active map.
  2. Add the group layer (.lyrx file) containing the Error Summary feature class, Error Locations feature class, Error Records table, and Error Resolutions table.
    By default, this file is in the folder specified in the Output Name parameter when the Analyze Network Data tool was run.
  3. Right-click the Error Summary feature class in the Contents pane, and click Attributes.
    The attributes table for the Error Summary feature class opens.
  4. Identify a record with the Self-intersecting line error code, and select the row.
    The Error Summary multipoint feature and related rows in the Error Resolutions table are selected.
  5. Right-click the selected row in the Error Summary attribute table and click Zoom To.
    The map zooms to display all summary records associated with the error.
    You can review each summary feature individually to better understand the error using the associated Error Locations features and Error Records table.
  6. Right-click the Error Resolutions table in the Contents pane, and click Open.
    The attributes table for the Error Resolutions table opens.
  7. In the Error Resolutions table, use Show Selected Records to filter the table.
  8. For the selected records, identify the record with a Context value of Error, and review the Action attribute value.
    If you checked the Set default resolution actions parameter when running the Analyze Network Data tool, a default resolution action of Delete all but first is specified for the field. If not, choose this value from the drop-down list in the field. This action causes the Apply Error Resolutions tool to delete all but the first vertex for the line at the intersecting location.
  9. On the ribbon, in the Manage Edits group, click Save to save your edits.
Resolution actions have been defined for errors found by the Analyze Network Data tool. You can use the Error Resolutions table as input for the Apply Error Resolutions tool to edit the utility network data and resolve the errors.
Learn more about how to apply error resolutions