Add machines to an ArcGIS Data Store type

ArcGIS Data Store allows you to create highly available or scalable data stores by including more than one machine in each type of data store that you deploy.

Options for adding machines vary by data store type and are explained below.

Relational store

The relational store is always deployed in primary-standby mode. The first machine on which you install ArcGIS Data Store and create a relational store is the primary relational store machine. You can install and configure one other relational store with the same GIS Server site, making this second relational store machine the standby machine. Data is replicated from the primary to the standby machine.

In the following diagram, the orange data store is the primary. It replicates data to the standby (the blue data store), and writes backup files to a cloud storage location.

Data is replicated from the primary to the standby machine.

If the primary machine becomes unavailable (for example, if it crashes, loses power, or loses network connectivity), the standby machine is promoted to primary. You will only be without the data for the period of time it takes for the standby machine to become the primary—this can take up to a few minutes. Once the standby becomes the primary relational store machine, it sends its backup files to the same location as the former primary machine, as shown below.

Standby machine becomes primary when primary is inaccessible.

If you can correct the problem with the former primary machine—for example, if the machine was unplugged and you plugged it back in, or the machine temporarily lost network connectivity but network connectivity was later restored—the former primary becomes the standby machine for the relational store.

If you cannot correct the problem—for example, the machine crashes and cannot be recovered—use the removemachine utility to unregister the failed machine. Configure a new relational store machine to act as the standby machine.

If you have configured a cloud relational store, hosted feature services remain available if the primary machine fails, even if you have not configured a standby machine, because the relational data is stored in the cloud database service. Some capabilities, however, depend on the additional system stores that are installed with the ArcGIS Data Store relational store. These capabilities, such as webhooks, will be unavailable if the primary machine fails and you have not configured a standby machine.

For information about when a relational store fails over, see ArcGIS Data Store deployment modes.

Object store

You can create an object store that contains one machine or you can deploy an object store in cluster mode that contains three or more machines.

A single-machine object store with a large amount of disk space and RAM can provide adequate performance. If you require scalability to allow the object store to grow as needed, deploy the object store in cluster mode instead.

Deploying the object store in cluster mode also allows it to be highly available.

When you deploy the object store in cluster mode, it must contain at least three machines. If one machine fails, existing hosted 3D layers remain available and response caching will continue to function. However, because the object store requires at least three healthy nodes to perform write operations, new hosted layers that rely on the object store cannot be published until the failed machine is recovered or replaced.

If you scale the object store to four or more machines and one machine fails, existing hosted 3D layers will remain available, hosted 3D layer types that support editing can continue to be edited, and new web layers that rely on the object store can continue to be published. Scaling beyond three machines also increases the storage capacity of the object store cluster.

Tip:
  • If one machine in the object store cluster fails and cannot be recovered, you can install ArcGIS Data Store on a new machine and configure it as part of the object store cluster using the same hosting server.

  • If the cluster contains only three machines, you must add a new machine to the cluster before you can run the removemachine utility to remove the failed machine.

Spatiotemporal big data store

The spatiotemporal big data store is always deployed in cluster mode. You can install ArcGIS Data Store on several machines, create spatiotemporal big data stores on each, and register each one with the same hosting GIS Server site.

Data in the spatiotemporal big data store is duplicated on at least two spatiotemporal big data store machines registered to the same hosting server.

Spatiotemporal big data store containing five machines

If any one machine fails, data still exists on at least one other machine. The data store replicates the data to another machine that is still functional.

One machine fails; data moved to remaining machines.

If the machine comes back online, it rejoins the cluster and data is rebalanced.

If the failed machine cannot be recovered, you can install ArcGIS Data Store on more machines and create spatiotemporal big data stores that are registered with the same hosting GIS Server site. In this example, three machines are added: one to replace the one that failed, and two more to accommodate increased numbers of hosted spatiotemporal feature layers. Data is rebalanced across all seven machines. Data for newly published spatiotemporal feature layers is also distributed.

Add machines to spatiotemporal big data store and data redistributes

Note:

If you script the creation of multiple machines in a spatiotemporal big data store, graph store, or object store, the first machine must be manually configured with the GIS Server site before you can script the creation of additional machines in the cluster. Include wait times in your script to be sure the additional machines are not added at the same time.

Machine roles

In a spatiotemporal big data store cluster, there are two roles: coordinator and data.

  • Coordinator—The coordinator keeps track of what machines are in or have been removed from the cluster and the health of each machine. The coordinator also controls the distribution of data across the cluster and rebalancing data when a machine is lost or removed.

    Machines that fill the coordinator role experience higher network traffic as a result of the communication required to manage all the machines in the cluster.

    A spatiotemporal big data store must contain at least one coordinator machine, must contain an odd number of coordinator machines, and can contain a maximum of five coordinator machines. Given these requirements, that means that a spatiotemporal big data store cluster can contain one, three, or five machines that have the coordinator role assigned to them.

    The first coordinator machine added to the cluster will be the current coordinator of the cluster; one of the other machines assigned the coordinator role can take over if the current coordinator machine is lost or removed from the cluster.

  • Data—Data machines store and search the spatial and nonspatial tables that populate hosted spatiotemporal layers. Machines that fill the data role must have a large amount of memory and processing power.

A machine can fill either role or both roles.

When you create a spatiotemporal big data store machine using the Data Store configuration app, the first three machines are created in both roles. In other words, all three machines will store data, the first machine will also serve as the current coordinator, and either of the other two machines can be promoted to coordinator if the current coordinator machine fails. Starting with the fourth machine, all machines added to the cluster using the Data Store configuration app are deployed in the data role only.

To control the role filled by a particular machine in the cluster when you create it, use the configuredatastore utility to create the spatiotemporal big data store. For example, you can run the configuredatastore utility to create the first three machines in the coordinator role only and create two more machines in the data role only, for a total of a five-machine cluster. This configuration isolates the network communications that could slow performance when the coordinator and data roles are filled by the same machine. It also allows you to have extra resources on the data only machines where they are most needed.

You can also use the configuredatastore utility to change the role of an existing, healthy spatiotemporal big data machine.

Supported role changes are as follows:

  • Specify --roles data to change a coordinator to a data machine. This is possible if there are other coordinator-eligible machines in the cluster. You can change a coordinator machine to a data role if there are at least three other coordinator-eligible machines in the cluster.

  • Specify --roles data to remove the coordinator role from a machine that was deployed with both roles. This leaves the machine in the data role. You can remove the coordinator role from the machine if there are at least three other coordinator-eligible machines in the cluster.

  • Specify --roles coord,data to add the coordinator role to a machine that was initially deployed to fill only the data role. A maximum of five machines can include the coordinator role. If there are already five coordinator machines in the cluster, you cannot add the coordinator role to a data machine in the cluster.

Run the describedatastore utility on any machine in the cluster to identify which machines are assigned the coordinator role, which are assigned the data role, and which machine is the current coordinator for the cluster.

You can only remove the coordinator role from a machine if there are three other coordinators in the cluster. In other words, if there are three machines that fill both the coordinator and data roles in the cluster, you cannot remove the coordinator role from any of those machines.

The number of machines in the cluster affects the status of the cluster when a machine fails and affects what role you can assign to the replacement machine.

In a cluster with only one coordinator machine, failure of that machine renders the spatiotemporal big data store unusable. You must add the coordinator role to at least two of the remaining machines or add two machines in the coordinator role to the cluster to bring the spatiotemporal big data store back online. Therefore, it is recommended that you have three or five machines in the coordinator role in the cluster. These machines can be in both the coordinator and data role or, if you have other machines in the cluster that fill the data role, they can be in just the coordinator role.

You must have at least two data machines in the cluster to prevent data loss if a data machine fails. In a cluster with only two data machines, when one data machine fails, add at least one new data machine to the cluster. If you do not add at least one data machine, you risk losing data if the remaining data machine fails. When there is only one data machine in the cluster, the only way to recover the data if the data machine fails is to restore the spatiotemporal big data store from a backup.

Graph store

The graph store can contain one machine (single instance) or three or more machines (cluster). If you require a highly available graph store, configure a graph store that contains at least three machines.

By default, when you install ArcGIS Data Store and create a graph store, it is created in single instance mode, but you can deploy in cluster mode instead. When you deploy in cluster mode, you must install and configure at least two other graph store machines with the same hosting GIS Server site. The graph store is not functional until it contains three machines.

If you deploy in single instance mode, you can use the configuredatastore utility to change the graph store to cluster mode.

Note:

You must have a default backup location configured for the graph store before you can change the graph store from single instance to cluster mode. You cannot change the graph store from cluster mode to single instance mode.

If the cluster contains three machines, and a machine in the cluster fails, data still exists on at least one of the other machines in the cluster. At this point, the graph store is in an unhealthy, read-only state, but existing graph layers continue to function. If the failed machine recovers—for example, it was temporarily unavailable due to a network issue that was corrected—the graph store cluster returns to a healthy state.

If the failed machine cannot be recovered, you must do the following to maintain the required minimum three machines in the graph store cluster:

  • First, run the removemachine utility to remove the failed machine from the cluster. This marks the machine for deletion.

  • Configure a graph store on a new machine and add it to the cluster. The machine that was marked for removal is now unregistered from the graph store cluster.

If two machines in a three-machine cluster fail and cannot be recovered, the graph store is no longer functional. You cannot remove and replace the two machines. You must restore the graph store from a backup.

Add a machine to a data store

Use the Data Store configuration app or the configuredatastore utility to add a machine to an ArcGIS Data Store type.

You can have one standby relational store machine. You can have multiple machines in a spatiotemporal big data store and in an object store and graph store that are running in cluster mode. All machines that participate in the same data store must use the same operating system and be the same ArcGIS Data Store release.

Use the Data Store configuration app to add a machine to a data store

Follow the steps below to use the Data Store configuration app to add a machine to a data store.

  1. Install ArcGIS Data Store on another server.

    Each standby machine, primary machine, or node in a cluster must be installed on different physical servers. Use the same network account for the ArcGIS Data Store account on all machines in the data store.

  2. Open the ArcGIS Data Store configuration app.

  3. Specify the fully qualified name of one of the machines in the GIS Server site that is acting as the ArcGIS Enterprise hosting server.

    The name is in the format gisserver.example.com. Use the same GIS Server site as you did when configuring the other machine or machines in the same data store for this ArcGIS Enterprise deployment.

  4. Type the username and password of the ArcGIS Server primary site administrator and click Next.

  5. Choose the type of data store to create.

  6. Specify a location for the new data store's directory and click Next.

  7. Review the information in the Configuration Summary. If it is correct, click Finish. If changes are needed, click Back to make corrections.

    The High Availability Role indicates that this is a standby machine for relational stores.

When the setup completes successfully, you have an additional data store machine to which ArcGIS Data Store can replicate data or caches.

If there were errors with the setup, click Next on the Configuration Summary dialog box to reopen the Data Store configuration app so you can provide different information. See Common deploy questions for causes and resolutions to setup errors.

Use the configuredatastore utility to add a machine to a data store

You can install ArcGIS Data Store on another server or servers and use the configuredatastore utility to add it to an existing data store. The utility is installed in <ArcGIS Data Store installation directory>\arcgis\datastore\tools.

You can install ArcGIS Data Store on another server or servers and use the configuredatastore utility to add it to an existing data store. The utility is installed in <ArcGIS Data Store installation directory>/tools.

Each standby machine, primary machine, or node in a cluster must be installed on different physical servers.

Note:

You must use the same network account for the ArcGIS Data Store account on all machines in the data store.

Follow these steps to use the configuredatastore utility to add a machine to a data store:

  1. Open a command shell on the additional server where you installed ArcGIS Data Store.

  2. Open a Command Prompt using the Run As Administrator option on the additional server where you installed ArcGIS Data Store.

  3. Run the configuredatastore utility, and provide the fully qualified domain name of a machine in the GIS Server site that is acting as the hosting server, and provide the ArcGIS Server primary site administrator username and password.

    Use the --stores operation to specify the type of data store to be created.

    You must specify the same GIS Server machine name and data store type that you used for the data store to which you want to add this machine.

    For example, the following adds a standby relational store to a machine in the GIS Server site with the fully qualified name of agsserver.ntwk.com. The data store directory on this machine is /home/dsuser/fsdata.

    /configuredatastore agsserver.ntwk.com siteadmin P$@pass /home/dsuser/fsdata --stores relational

    For example, the following adds a standby relational store to a machine in the GIS Server site with fully qualified name agsserver.ntwk.com. The data store directory on this machine is c:\data\.

    configuredatastore agsserver.ntwk.com siteadmin P$@pass c:\data\ --stores relational

Another data store machine is added to the data store.