Skip to main content

Use geoprocessing models to manage diagram template rule and layout definitions

You can create diagram templates by running individual geoprocessing tools. This process is typically the following: In the Geoprocessing pane, run the Add Diagram Template tool, and run the Add <XXX> Rule or Add <XXX> Layout tool. Through this process, each rule is added in a systematic order because the sequence of rules for a template is arranged based on the order in which the rule was added; in other words, each newly added rule is appended to the end of the template rule sequence. Additionally, each newly added layout is appended to the end of the template layout sequence based on the order in which the layout is added.

However, for greater control over your template configuration and to document its structure, it is strongly recommended that you use ModelBuilder to create a geoprocessing model of your diagram template's rule and layout definitions. A geoprocessing model functions in a similar manner to the network diagrams building process. Both operations provide organization and structure for three main phases:

  • Phase 1—Create a template and configure its elementary properties.

  • Phase 2—Add rules that define the final diagram content.

  • Phase 3—Add the set of diagram layouts that generate the presentation (spacing, visibility, and so on) of a diagram.

Three phases of the diagram template's rule and layout definitions geoprocessing model

To control the creation process of your templates, the set of tools in a diagram template's rule and layout definitions geoprocessing model must be chained so that the output network and diagram template of the previous tool are the inputs to the next tool. This allows you to ensure the exact order of each rule in the template rule sequence as well as each layout in the template layout sequence. It results in better control over the content and its layout in the diagrams later based on this template.

Requirements and prerequisites

Adding diagram templates and editing their rule and layout definitions are administration and configuration tasks.

The requirements and prerequisites to configure a diagram template—for example, to create, alter, add rules or layouts to its definitions, export and import those definitions, and so on—are the same:

  • This operation must be run from either a utility network or trace network in a file or mobile geodatabase, or a database connection to the utility network or trace network in an enterprise geodatabase. When working with a utility network or trace network in an enterprise geodatabase, you can't work from a service.

  • For the case of a database connection to a utility network or trace network in an enterprise geodatabase, you must connect using the credentials of the database network owner; that is, using the database utility network owner or database trace network owner credentials.

  • When working with a database connection to a utility network or trace network in an enterprise geodatabase, you must sign in to your ArcGIS Enterprise portal using the credentials of the portal network owner; that is, using the portal utility network owner or portal trace network owner credentials.

Create a diagram template's rule and layout definitions geoprocessing model

The subsections below provide steps for each phase of the ModelBuilder workflow.

Phase 1—Create a template and configure its elementary properties

Before configuring the template geoprocessing model, the first step consists in running the Add Diagram Template tool to create the template itself:

  1. Start ArcGIS Pro.

  2. When working with a utility network or trace network in an enterprise geodatabase, sign in to your ArcGIS Enterprise portal using the credentials of the portal network owner—that is, using the portal utility network owner or portal trace network owner credentials.

  3. Load a project or create one.

  4. Depending on the geodatabase you want to work with, do one of the following:

    • When working with a utility network or trace network in a file or mobile geodatabase, add the file or mobile geodatabase to the project.

    • When working with a utility network or trace network in an enterprise geodatabase, add the database connection file to the project or create one.

      Caution:

      Make sure the utility network or trace network is registered as branch versioned and you are connecting using the credentials of the database network owner—that is, using the database utility network owner or database trace network owner credentials.

  5. Open the Geoprocessing pane, click Toolboxes, and expand the Network Diagram Tools toolbox.

  6. Expand the Configuration toolset and load the Add Diagram Template tool to the model view.

    1. Click the browse button next to the Input Network box, go to Project/Databases, select the database connection file, and browse to the network.

    2. Type a name for the new template in the Diagram Template Name box.

    3. Click Run.

The next workflow steps take place in a new geoprocessing model edited using ModelBuilder. Such a template geoprocessing model starts using the Alter Diagram Template tool:

  1. On the Analysis tab, click ModelBuilder.

    A new geoprocessing model view named Model opens.

  2. From the Configuration toolset under the Network Diagram Tools toolbox, drag the Alter Diagram Template tool to the model view.

  3. Double-click the Alter Diagram Template box.

  4. Click the browse button next to the Input Network box, go to Project/Databases, select the database connection file, and browse to the network.

  5. From the Input Diagram template list, select the name of the diagram template you have just created.

  6. Check the Remove the diagram template rule and layout definitions option.

    Caution:

    Removing the rule and layout definitions at the very beginning of the geoprocessing tool sequence allows you to make sure that the sequence of rules and layouts currently set up in the geoprocessing model will be those initialized on the template.

    When rerunning the diagram template geoprocessing model without checking this box, each rule and layout processed is added to the end of the template rule and layout sequences that could already exist on the template, causing the same set of rules and layouts to be configured several times. This makes the content of diagrams based on the template unsuitable.

  7. Consider the other options:

    1. Check Default template if you want this new template to be the default diagram template.

    2. In the Description text box, type a description for your diagram template.

  8. Expand the Template General Definitions section.

    1. Depending on your network coordinate system, type an appropriate value for the container margin size.

      For example, type 0.2 for Container Margin and select Meters from the drop-down list.

    2. Uncheck Enable diagram storage if you want to prevent users from storing diagrams based on this template. Typically, this makes sense if your template is designed to generate a single diagram for data control purposes.

    3. Check Enable to extend diagram if you want users to be able to extend diagrams based on this template.

  9. For the case the diagram template will be used to generate circuit diagrams, consider the options in the Template Telecom Domain Association section.

  10. Click OK.

Your diagram template geoprocessing model should look like the following:

Phase 1 example diagram template's rule and layout definitions geoprocessing model

Phase 2—Add rules that define the final diagram content

The second phase in the configuration of a diagram template's rule and layout definitions geoprocessing model is dedicated to rules. It uses tools such as Add <XXX> Rule or Add <XXX> By Attribute Rule to add a new rule to the template rule sequence. The sequence of rules created by these tools defines the order in which the diagram building process will run the rules, defining the content of diagrams based on that template.

Rules are used to modify the diagram graph, but each rule operates a specific transformation of the graph that often justifies a common position in the rule sequence. For example, a Trace rule is generally set up at the beginning of the template rule sequence, Reduce Junction rules are often configured at the end of the rule sequence, and Remove Feature rules can be set up at any position in the sequence depending on their purpose.

As detailed in Diagram rules, the process of each rule in this chain is iterative, but the rule sequence is not. To adopt an iterative rule sequence, two additional tools are often used during this phase—Add Start Iteration Rule and Add Stop Iteration Rule. These tools must be used to iterate a sequence of multiple Reduce Junction rules that don't only process junctions connecting two other junctions; in other words, when among the Reduce Junction rules, there are junctions with one adjacent junction that are configured to be reduced. Reducing the junctions connecting one other junction causes the number of connections to the remaining junctions to change, so those remaining junctions potentially become new candidates for a reduction rule that was run beforehand.

Keeping in mind that each rule is optional, most of the typical rule sequences you will configure should fit all or part of the sequence detailed below:

  1. Remove Features rules—Configured using the Add Remove Feature Rule, Add Remove Feature By Attribute Rule or Add Remove Feature By Category Rule tools, Remove Features rules can be run at the first position of the rule sequence to systematically discard particular network features or network objects from the diagram before refining the diagram graph.

    For example, apply the Add Remove Feature Rule tool with the Exclude source classes rule process to discard any network features or network objects related to all network source classes and object tables except some specific network source classes or object tables. Also, since graph completeness is always maintained in network diagrams, excluding a particular line class (for example, a transmission line) while running Source Type = EDGES may be helpful to ensure your diagrams build on a given part of the network, in other words, the transmission network in this example.

  2. Spatial Query rules—Added using the Add Spatial Query Rule tool, Spatial Query rules can be set up in the rule sequence at any time but may be useful at the beginning of the rule sequence to include all features of interest.

  3. Trace rules—Added using the Add Trace Rule tool, Trace rules are generally one of the first rules you set up in the rule sequence when you want to configure a template to generate diagrams from traces. In this case, you can also configure Set Starting Point rules on the template to set specific features or junction terminals as starting points for the Trace rule to process. Starting Points rules must be set up before the Trace rule in the diagram template rule sequence using the Add Set Starting Point By Attribute Rule tool.

  4. Expand Containers rules—Configured using the Add Expand Container Rule, Add Expand Container By Attribute Rule or Add Expand Container By Category Rule tool, Expand Containers rules allow you to expand containers in diagrams. They are generally set up before any rules that simplify the diagram graph.

  5. Add Connectivity Associations rule—Configured using the Add Connectivity Associations Rule tool, Add Connectivity Associations rules can be set up to get the connectivity associations represented in the diagrams and ensure graph completeness before collapsing or reducing features.

    Caution:

    Avoid configuring this rule when it is not needed because it is time-consuming. For example, adding connectivity associations is not relevant to a template configured to run a Trace rule, since the connectivity associations will already be systematically returned by the trace.

  6. Add Diagram Feature Capability rules—Added using the Add Diagram Feature Capability By Attribute Rule or Add Diagrarm Feature Capability By Category Rule tool, Add Diagram Feature Capability rules can be set up to manage collapsing of containers or reduction of junctions with precision. They can be used to prevent particular containers from collapse or particular junctions to be reduced during all or part of the diagram building.

  7. Collapse Containers rules—Set up when running the Add Collapse Container Rule, Add Collapse Container By Attribute Rule or Add Collapse Container By Category Rule tool, Collapse Container rules are run to collapse containers in diagrams. They must be performed after the Expand Container rules if you want to keep track of all contents related to the collapsed containers.

  8. Start Iteration rules—Configured using the Add Start Iteration Rule tool, the Start Iteration rule must be positioned at the beginning of a Reduce Junction rule iterative sequence. It forces the building diagram process to loop on the Reduce Junction rule sequence until there are junctions in the diagram, which is reduced by one of the rules in that sequence.

  9. Reduce Junction rules—Added when running the Add Reduce Junction Rule, Add Reduce Junction By Attribute Rule and Add Reduce Junction By Category Rule tools, Reduce Junction rules are used to simplify the diagram graph.

    Caution:

    During configuration, do not use Reduce Junction rules that process junctions connecting a maximum of two other junctions with Reduce Junction rules that process a minimum of three other junctions inside the same reduction rules' iterative sequence. Using these together decreases performance at diagram generation. To reduce junctions connecting a minimum of three other junctions, set up two iterative sequences—the first one to process the reduction of junctions connecting a maximum of two other junctions and the second for the reduction of junctions connecting a minimum of three other junctions.

    Tip:

    Because content diagram junctions do not aggregate noncontent diagram features, you can configure a Remove Feature rule before reducing junctions to remove any polygon containers and all content-container relations in the diagram and force reductions.

  10. Stop Iteration rules—Configured using the Add Stop Iteration Rule tool, Stop Iteration rules must be positioned at the end of a Reduce Junction rule iterative sequence, in other words, just after the last Reduce Junction rule in the sequence where you want the build process to iterate.

  11. Reduce Edge rules—Set up using the Add Reduce Edge By Attribute Rule tool, Reduce Edge rules reduce edges.

  12. Structural Attachment rules—Configured using the Add Structural Attachments Rule tool, Structural Attachment rules are systematically run last wherever they are set up in the rule sequence.

    Caution:

    Avoid configuring this rule when it is not needed because it is time-consuming. For example, adding structural attachments is not relevant to a template configured to run the following:

    • A Trace rule that does not include structures

    • Remove Feature rules set up to process structure junctions that support attachments

Note:

You can also set up Remove Feature rules under these specific circumstances:

  • After a Trace rule or after an Expand Containers rule to remove container relations in the diagram graph. This simplifies the diagram graph.

  • At the end of your rule sequence to clean the diagram graph or simplify the diagram, for example, to systematically remove linear container edges, since having both the network linear containers and their related contents represented in the diagrams may be confusing or irrelevant.

The following diagram illustrates the recommended position for each rule in the rule sequence according to the recommendations outlined above:

Recommended position for each rule in a rule sequence

Example of adding diagram rules to a diagram template

The steps below are an example of adding diagram rules to a diagram template. The purpose of this sample is to chain the Add <XXX> Rule or Add <XXX> By Attribute Rule tool in a diagram template to allow the generation of diagrams from a subnetwork trace that starts from the circuit breakers among the input features. The resulting trace will then be simplified by collapsing most of the containers and reducing junctions and devices, except circuit breakers and switches. To ensure the diagrams based on this template will strictly reflect the expected subnetwork traces, some Remove Feature rules will be configured at the beginning of diagram generation to discard all unexpected input features.

Prerequisite:

Create an elementary diagram template geoprocessing model as described in Phase 1—Create a template and configure its elementary properties before applying the next steps.

  1. Open the diagram template geoprocessing model you created in the previous section.

  2. Configure diagram rules to remove any unexpected features that may have been selected as input. In this example, Remove Feature rules are set up to discard all input features, except structure boundaries and circuit breaker distribution devices:

    1. In the Configuration toolset, drag the Add Remove Feature Rule tool to the model view.

    2. Connect the output variables of the Alter Diagram Template tool to the Add Remove Feature Rule tool as follows:

      • Click the output network variable of the Alter Diagram Template tool while you move the pointer to the Add Remove Feature Rule tool. Click Input Network.

      • Click the output template variable of the Alter Diagram Template tool while you move the pointer to the Add Remove Feature Rule tool. Click Input Diagram Template.

    3. Double-click the Add Remove Feature Rule tool in the model and set the rule parameters to remove all features except electric distribution devices and structure boundaries as follows:

      • Source Type—Select Both junctions and edges.

      • Rule Process—Select Exclude source classes.

      • Network Sources—Select ElectricDistributionDevice, and select Structure Boundary.

    4. Click OK.

    5. In the Configuration toolset, drag the Add Remove Feature By Attribute Rule tool to the model view.

    6. Repeat steps 2.b above to connect the output variables of the Add Remove Feature Rule tool as inputs for the Add Remove Feature By Attribute Rule tool.

    7. Double-click the Add Remove Feature By Attribute Rule tool in the model and set the rule parameters to remove any electric distribution devices except circuit breakers:

      • Network Source To Remove—Select ElectricDistributionDevice.

      • Expression—Click New Expression. Then select Asset group for Field, and click Is not equal to as the expression operator. Check 4 - CircuitBreaker for Values, and click Update.

    8. Click OK.

  3. Set the starting points among the features that will remain. In this example, a Set Starting Point rule is configured to set any circuit breaker with a terminal ID of 3/ Load as a starting point:

    1. From the Configuration toolset, drag the Add Set Starting Point By Attribute Rule tool to the Model tab.

    2. Connect the output variables from Add Remove Feature By Attribute Rule as input for Add Set Starting Point By Attribute Rule.

    3. Double-click the Add Set Starting Point By Attribute Rule tool in the model and set the rule parameters:

      • Network Source—Select ElectricDistributionDevice.

      • Expression—Click New Expression. Then select Asset group for Field, and click Is equal to as the expression operator. Check 4 - CircuitBreaker for Values, and click Update.

      • Junction Terminal(s)—Check 3/Load.

    4. Click OK.

  4. Add a Trace rule to trace medium-voltage distribution subnetworks:

    1. Double-click the Add Trace Rule tool in the model and set up a Trace rule to trace subnetworks as follows:

      • Trace Type—Select SUBNETWORK.

      • Domain Network—Select ElectricDistribution.

      • Tier—Select Medium Voltage.

    2. Click OK.

  5. Collapse containers. In this example, the Collapse Containers rule is configured to collapse all containers except structure boundaries:

    1. In the Configuration toolset, drag the Add Collapse Container Rule tool to the model view.

    2. Connect the output variables from Add Trace Rule as input for Add Collapse Container Rule.

    3. Double-click the Add Collapse Container Rule tool in the model and set the rule parameters:

      • Container Type—Select Both junctions and edges.

      • Rule Process—Select Exclude source classes.

      • Container Sources—Select StructureBoundary.

      • Aggregate reconnected edges—Leave the box checked.

    4. Click OK.

  6. Loop on a sequence of reduction rules to reduce all junctions that have 0, 1, or 2 other junctions, except distribution devices and assemblies; reduce all distribution assemblies except the switch gears and switch banks; and reduce all distribution devices except the circuit breakers and switches:

    1. In the Configuration toolset, drag the Add Start Iteration Rule tool to the model view.

    2. Connect the output variables from Add Collapse Container Rule as input for Add Start Iteration Rule.

    3. In the Configuration toolset, drag the Add Reduce Junction Rule tool to the model view.

    4. Connect the output variables from Add Start Iteration Rule as input for Add Reduce Junction Rule.

    5. Double-click the Add Reduce Junction Rule tool in the model and set the rule parameters:

      • Rule Process—Select Exclude source classes.

      • Junction Sources—Select ElectricDistributionDevice and select ElectricDistributionAssembly.

      • Connectivity constraints—Expand this section:

        • Reduce Junctions With—Select Maximum two connected junctions.

        • Reduce if unconnected—Check the box.

        • Reduce if connected to a single junction—Check the box.

        • Reduce if connected to 2 different junctions—Leave the box checked.

    6. Click OK.

    7. In the Configuration toolset, drag the Add Reduce Junction By Attribute Rule tool to the model view.

    8. Connect the output variables from Add Reduce Junction Rule as input for Add Reduce Junction By Attribute Rule.

    9. Double-click the Add Reduce Junction By Attribute Rule tool in the model and set the rule parameters:

      • Junction Source To Reduce—Select ElectricDistributionAssembly.

      • Expression—Click New Expression. Then select Asset group for Field and click Does not include the value(s) as the expression operator. Check 8 - Switch bank and 9 - Switchgear for Values and click Update.

      • Connectivity constraints—Expand this section:

        • Reduce Junctions With—Select Maximum two connected junctions.

        • Reduce if unconnected—Check this box.

        • Reduce if connected to a single junction—Check this box.

        • Reduce if connected to 2 different junctions—Leave this box checked.

    10. Click OK.

    11. In the Configuration toolset, drag the Add Reduce Junction By Attribute Rule tool to the model view.

    12. Connect the output variables from the first Add Reduce Junction By Attribute Rule as input for the second Add Reduce Junction By Attribute Rule.

    13. Double-click the second Add Reduce Junction By Attribute Rule tool in the model and set the rule parameters:

      • Junction Source To Reduce—Select ElectricDistributionDevice.

      • Expression—Click New Expression, select Asset group for Field, and click Does not include the value(s) as the expression operator. Check 4 - Circuit Breaker and 15 - Switch for Values and click Update.

      • Connectivity constraints—Expand this section:

        • Reduce Junctions With—Select Maximum two connected junctions.

        • Reduce if unconnected—Check this box.

        • Reduce if connected to a single junction—Check this box.

        • Reduce if connected to 2 different junctions—Leave this box checked.

    14. Click OK.

    15. In the Configuration toolset, drag the Add Stop Iteration Rule tool to the model view.

    16. Connect the output variables from Add Reduce Junction By Attribute Rule as input for Add Stop Iteration Rule.

The second phase of your diagram template geoprocessing model should look similar to the following:

Phase 2 example diagram template's rule and layout definitions geoprocessing model

Phase 3—Add the set of diagram layouts

The third phase of your template configuration is dedicated to layouts. This consists of defining the set of active layouts with their parameter values and presetting default parameter values for those added as inactive layouts. It is configured using the Add <XXX> Layout tools, which allow a new layout to be added to a template layout sequence. The only exception is the Add Diagram Feature Selection To Layout tool that can be used before any active layout to filter out the diagram feature selection to which this active layout applies.

Note that the Set Root Junction rule is tied to certain layouts that can be set up during this third phase. It is configured using the Add Set Root Junction Rule By Attribute Rule tool. This rule allows you to flag junctions in the generated diagrams as root junctions that can then be taken into account by the layouts you set up to apply to the diagrams.

As with the rules phase, the layouts phase must be carefully set up when configuring diagram templates. It is recommended that you proceed in the following order:

  1. To apply any tree layout during the diagram building process; for example, Smart Tree, Radial Tree, Mainline Tree, and make this Tree layout starts from specific junctions, use the Add Set Root Junction Rule By Attribute Rule tool to query and identify the roots.

    Note:

    This tool can be added at any position along the rule sequence and not only at the very end of that sequence before you start configuring the layout sequence. As an example, you configured a Trace rule to start from subnetwork controllers provided as inputs and want to lay out your diagram as a tree starting from the input subnetwork controllers. In this case, set the Add Set Root Junction Rule By Attribute Rule tool before the Add Trace Rule tool to query the only subnetwork controllers that users will provide as inputs. Indeed, the trace rule that applies later may return other subnetwork controllers that you do not want to be used as tree roots. If the Set Root Junction rule is configured to run after the Trace rule, you may have no way to set up the SQL expression to properly query the only input subnetwork controllers you expect among all the subnetwork controllers that exist at that time in the diagram.

  2. To configure an active layout and make it applies only to particular diagram feature selection set, use the Add Diagram Feature Selection To Layout tool to filter out those particular diagram features before configuring the active layout.

    Note:

    You may have to chain multiple Add Diagram Feature Selection To Layout tools to filter out all the diagram features you expect to be laid out by the next active layout.

  3. Set up the sequence of active layout algorithms in the order you want them to apply during the diagram generation—when running the appropriate Add <XXX> Layout tool with the Active option enabled.

    Note:

    If you select a set of diagram features to layout using the Add Diagram Feature Selection To Layout tool and configure multiple layouts to be chained during diagram building, only the first active layout in the layout sequence applies to this selection set. The selection set is systematically clear at the end of the first active layout process and the next layouts apply to all the diagram features. To make multiple layouts apply to the same set of diagram features, you must configure the Add Diagram Feature Selection To Layout tools before each active layout you want to chain.

  4. Set up the list of inactive layout algorithms—when running the appropriate Add <XXX> Layout tool with the Active option disabled.

Note:

To maintain your diagram template geoprocessing model in the future, do not mix active and inactive layouts.

Note:

When configuring any sequence of active layout algorithms, keep the following in mind:

  • There is no benefit to configure schematic layouts that preserve or try to preserve the current positions of the diagram features—for example, Linear Dispatch, Spatial Dispatch, and so on—before a tree layout, such as Radial Tree, Smart Tree, and Mainline Tree layouts.

  • Partial Overlapping Edges and Reshape Diagram Edges layouts are often used as active refining algorithms run at the last position in the template layout sequence.

As an example, the steps below describe the template configuration geoprocessing tools that must be chained together to lay out the generated diagram content as a smart tree, starting with circuit breakers as root junctions with tree branches arranged from the top to the bottom, and in which all the edges that may become overlapping after the Smart Tree layout completion are systematically separated.

Example of adding diagram layouts to a diagram template

The steps below are an example of adding diagram layouts to a diagram template. The purpose of this sample is to identify circuit breakers existing in the diagram and set them as root junctions, apply a Smart Tree layout, and separate diagram edges that can overlapping each others in the diagram.

Prerequisite:

Create a diagram template geoprocessing model as described in Phase 1—Create a template and configure its elementary properties and Phase 2—Add rules that define the final diagram content before applying the next steps.

  1. Open the diagram template geoprocessing model you created in the previous section.

  2. In the Configuration toolset, drag the Add Set Root Junction By Attribute Rule tool to the model view.

  3. Use steps 10a and 10b from the Phase 1 workflow to connect output variables from Add Stop Iteration Rule as input for Add Set Root Junction By Attribute Rule.

  4. Double-click the Add Set Root Junction By Attribute Rule tool in the model and set up the Set Root Junction rule so it flags each circuit breaker as a junction root:

    1. Select DistributionDevice from the first drop-down list under Junction Source To Select.

    2. Click New Expression.

    3. Select Asset group for Field, click is Equal to as the expression operator, and check 4 - CircuitBreaker for Values. Click Update.

    4. Click OK.

  5. In the Configuration toolset, drag the Add Smart Tree Layout tool to the model view.

  6. Connect output variables from Add Set Root Junction By Attribute Rule as input for Add Smart Tree Layout.

  7. Double-click the Add Smart Tree Layout tool in the model and set up the layout algorithm so it arranges the tree branches from the top to the bottom:

    1. Leave the Active box checked so the algorithm activates during diagram generation.

    2. Select From top to bottom from the Tree Direction drop-down list.

    3. Click OK.

  8. In the Configuration toolset, drag the Add Reshape Diagram Edges Layout tool to the Model tab.

  9. Connect output variables from Add Smart Tree Layout as input for Add Reshape Diagram Edges Layout.

  10. Double-click the Add Reshape Diagram Edges Layout tool in the model and set up the layout algorithm so it separates edges that may be overlapping in the diagram:

    1. Leave the Active box checked so the algorithm activates during diagram generation.

    2. Select Separate overlapping edges from the Reshape Operation drop-down list.

    3. Click OK.

The third phase of your diagram template geoprocessing model should look similar to the following:

Phase 3 example diagram template's rule and layout definitions geoprocessing model

Run a diagram template's rule and layout definitions geoprocessing model

To run a diagram template geoprocessing model and generate diagrams based on this template, complete the following steps:

Prerequisite:

Create a diagram template's rule and layout definitions geoprocessing model as described in the section above and open it for editing.

  1. Click the ModelBuilder tab and click Validate.

  2. Click Run.

  3. Click Save to save the diagram template geoprocessing model in your project toolbox.

  4. Open the map that references the network from which you want to generate diagrams.

  5. To generate diagrams based on the new template, do one of the following:

    • Select some features on the network map or objects in the network source object tables referenced in the map. Then, choose the diagram template among the template list under the New drop-down list.

    • Starting with ArcGIS Pro 3.5 | ArcGIS Enterprise 11.5, set network elements as starting points. If needed, set network elements as barriers. Then, in the Diagram group, choose a diagram template among the template list under the Use Trace Locations drop-down list.

Verify that a new item corresponding to the name of the newly created template appears in the template lists and test the newly created template settings.

To make the template you just created fully operational for working with the related service, sign in to your ArcGIS Server Manager portal using the administrator credentials, and stop and restart this service.

Maintain a diagram template's rule and layout definitions geoprocessing model

All the geoprocessing models you build are saved in your ArcGIS Pro project toolbox by default. To avoid losing your diagram template geoprocessing model when this project is deleted, create your own toolbox in a safe location on your local disk, and keep a backup of all your diagram template geoprocessing models in this toolbox.

Note:

Starting with ArcGIS Pro 3.6, you can run the Create Geoprocessing Model From Diagram Template tool to re-create geoprocessing models with the sequence of network diagram configuration tools used to set up the diagram rules and diagram layouts currently configured on your diagram templates.